Alexiy,
А вот и текст для чтения:
то, что в начале про третью гармонику для снабжающих трансформаторов, - зеркально справедливо и для трансформатора в нагрузочной цепи, смысл второй части, я уже коротко изложил в предыдущем посте.
*All phase control dimmers are non-linear loads. A non-linear load is one where current is not in proportion to voltage. The non-linear load on dimming systems is caused by the fact that current is switched on for only part of the line cycle by a phase control dimming system. This non-linear load creates harmonic distortion on the service feeder.
Harmonics are currents that occur at multiples of the power line voltage frequency. In Europe where line frequency is 50 Hz the 2nd harmonic frequency is 100 Hz; the 3rd harmonic is 150 Hz, and so on. In North America where line frequency is 60 Hz the 2nd harmonic frequency is 120 Hz; the 3rd harmonic is 180 Hz, and so on.
Excess harmonic currents cause conductors and the steel cores of transformers and motors to heat.
...
Sometimes the heating of the distribution trasformer can be a problem, because transformers are rated for undistorted 50 Hz or 60 Hz load currents. When load currents are non-linear and have substantial harmonic content, they cause considerably more heating than the same undistorted current. In heavily dimmed system, you might not be able to ultilize more than around 70 % of the rated transformer power rating because of harmonic induced heating.
...
Normal light dimmers are designed to only dim non-lunductive loads like light bulbs and electric heaters. Normal light dimmers are not suitable to dim inductive loads like transformers, fluorescent lamps, neon lamps, halogen lamps with transformers and electric motors. There are special dimmers available for those applications.
If you connect inductive loads to the dimmer the dimmer might not work as expected (for example does not dim that load properly) and can even be damaged by the voltage surges generated by the inductive load when current changed radiply. Another problem is the phase shift between the voltage and current cause by the inductance. If you use a normal simple light dimmer which is just in series with the wire going to the load, this will cause that the dimmer circuit will not wirk properly with highly inductive loads. Special dimmers which have a separate controlling electronics connected to both live and neutral wire and then the triac which controls the current to the load usually work much bettter with inductive loads.
Often when inductive loads cause problems on normal dimmers, you can eliminate said problems by patching an incandescent "ballast" load in parallel with the inductive load. Usually 100W is enough for many inductive loads. Remeber that indictive loads can hum quite noticably when dimmed and the transformers can heat more because of increased harmonics content in the power coming to them.*